380VAC 3-phase off grid system. Is it possible with powerwall?

380VAC 3-phase off grid system. Is it possible with powerwall?

Hi,

I have a 12kwatt sollar system and I am interested in Tesla powerwall.

My consumption is 25 to 35kwatt/hour per day. Voltage: 380VAC 3phase (off grid). Peak power 5 to 7 kWatt per phase.

Is it possible with powerwall? How many powerwalls will I need and how I have to connect them.

Thank you for your time

Aristidis

eric.zucker | 24. November 2017

Tesla powerwalls do not natively support three phase grids yet.

jp | 26. Dezember 2017

The PW2's do not natively generate a 3phase output. In addition - ganging 3 PW2's together requires 3 gateways (one per phase) and they can only track a single existing AC phase, not ofsetting by 120degrees from another source.
I'd also speculate that trying to hook them in some sort of y configuration (as domestic installs are) is likely to be both spectacular and short-lived, if it started at all. I'll be very interested in any 3phase solution they come up with as I'm using 2 PW in a 3phase setup now in a sorta 2-outta-3 phase arrangement, and whilst it works great there are some significant drawbacks.