220 volt outlet (NEMA 5-15) for tesla charging
I have 220 volt outlet (NEMA 5-15) outlet on 30amp breaker for bitcoin mining, can I use this outlet to charge tesla?
1
Comments
https://teslatap.com/articles/home-charging-wiring-guide/#connectors
It sounds like you're on the right track. As @TT points out, assuming it is a 5-20, it is only 120 volts. You might check the breaker. As such, it will only charge at around 5 mph. You may be able to upgrade the breaker to a 240v/20a one and up your charging speed to about 10 mph which is quite reasonable for daily use.
> @davenest - Good to hear. If it is a dedicated outlet, it could be switched to a NEMA 6-20, and rewired in the breaker box for 240V to double the charging speed. No new wires between the outlet and the breaker box. It is critical that this be the only outlet or other outlets will destroy what is plugged into them!
Now that is a great idea! In fact the wire gauge needed 240V @ 20A (14 AWG) is smaller than what is needed for 120v @ 20A (12 AWG). Very cool idea @"TeslaTap.com"! I think the only issue is that 120V outlets are rarely dedicated, but that can be addressed.
@davenest - This is confusing. Both 5-15 and 5-20 are for 120 vac circuits. You must have either 6-15 or 6-20 for 240v circuits at 15 or 20 amps respectively.
Now you could incorrectly wire a NEMA 5-20 to 240v, but the outlet would allow any 120v item to be plugged in, and likely be destroyed and/or catch fire. Quite dangerous and not at all to code.
Tesla has adapters for both 6-15 and 6-20 outlets:
https://shop.tesla.com/product/gen-2-nema-adapters
In the past, Tesla cars don't care if it was anything up to 277 VAC or so, although it does look for voltage sag as an indication of an improper installation.
> It’s already 240v, but which adapter to use nema 5-15 or nema 5-20. The receptacle will take either..
Time for a call to a LICENSED electrician.
Note that a 5-20 outlet looks exactly like a 6-20 outlet unless you take great care.
A 5-20 outlet on a 240v circuit is a code violation and safety issue that should be corrected.
Weird setup. Did you do it yourself? Otherwise get a new electrician.